If you’d like to run your spindle in manual mode, flip the “Manual Override” switch up or “1” to enable VFD Keypad controls. Then use the Run/Stop and Potentiometer dial on the front of your VFD to run your motor.
If you’d like to automatically control your spindle via g-code and your Masso controller, perform the following wiring on the Masso G3 to wire in the control cable from the VFD.
Note: Tape the Orange wire off as it is not required.
VFD's GND => Black => GND
Shield Drain => GND
VFD's VF1 => Red => Pin 1
VFD's COM => White => Pin 4 & 6
VFD's DI1 (programmed as CW) => Yellow => Pin 5
VFD's DI2 (programmed as CCW) => Green => Pin 7
Use a jumper wire to link Pins 4 and 6 together.
The orange wire supplies 10v power and is not required by the Masso G3.
For Programming:
Under the F1 Screen Main Spindle,
Encoder (Pulses per revolution) = 100
Spindle Control = VFD
Maximum RPM = 24000
Spin UP delay = 6000
Spin DOWN delay = 6000