Home > Spindles & ATCs > Controller Guides for Automatic Control > Sienci Labs - SuperLongBoard(-ext) Controllers (aka AltMill's)
Manual Mode Operation
Wiring your Spindle to the SuperLongBoard(-ext) Controller for Automatic Mode Operation
Spindle System Wiring
Spindle Kit Wiring
This mode is where your CNC controller controls the VFD via Modbus/RS-485 communications connection signal.  For SuperLongBoard(-ext), your controller is able to control CW/Forward, CCW/Reverse, and the 0-24000rpms.
We have pre-programmed your VFD to run in automatic mode when the Manual Override switch is flipped to automatic (down or 0 position).  The vfd will digitally communicate with your SuperLongBoard(-ext) Controller over Modbus, also known as RS-485, for telling the spindle how fast it should spin and in which direction.  When your controller tells the spindle to stop moving... the VFD's will be in standby/stopped mode with a blinking keypad display.  When your controller tells the spindle to run at a certain speed, your VFD will be changed to spin/forward mode with a solid keypad display showing the RPMs it was told to spin the motor at.
P0.0.03 = 2
P0.0.04 = 9
P0.0.11 = 6
P2.0.02 = 21
P4.1.00 = 4
P4.1.01 = 3
Your VFD will now perform two-way communications with the SuperLongBoard(-ext) controller.  The controller now uses the Modbus/RS-485 wires to know how fast it should spin the motor as well as when to switch from Stopped/Standby to CW/Forward to CCW-Reverse.
When your VFD is told to switch from Run Mode the vfd will change from standby/stopped mode (blinking keypad display) to spin/forward mode (solid keypad display).
In Run Mode, the VFD will also spin the the commanded RPMs which will be displayed on the VFD's keypad.
Setting up your SuperLongBoard(-ext) Controller for Automatic Mode Operation
We have played with SuperLongBoard(-ext) controllers before and here are a few notes we've gathered as to how to configure it for controlling a spindle:
CONFIGURING gSender (grblHAL Modbus)
Modbus requires correct firmware configuration.
We strongly recommend exporting your current settings before making changes:
gSender → Config → Export
This will produce a .json file with your settings inside.
Known Working grblHAL Settings
The following values must match exactly:
$16 = 0
$30 = 24000
$31 = 6000
$340 = 0
$374 = 19200
$375 = 50
$392 = 6
$395 = MODVFD
$462 = 40960
$463 = 40961
$464 = 36864
$465 = 1
$466 = 2
$467 = 6
$468 = 25
$476 = 1
If $476 is unavailable, check neighboring parameter $478 for spindle address.
Baud rate must match between VFD and grblHAL.
If any value differs, correct it and reboot the controller.
ALARM 14 – WHAT IT MEANS
Alarm 14 in grblHAL is:  “Spindle at Speed Timeout
This means:
The controller did not receive confirmation from the VFD that the spindle reached commanded speed within the allowed time.
Alarm 14 does NOT automatically mean:
• The spindle is defective
• The VFD is defective
• The motor is wired incorrectly
If manual mode works, this alarm is a Modbus communication configuration issue.
Common causes:
• Baud rate mismatch
• Slave ID mismatch
• Incorrect register mapping
• Spindle-at-speed confirmation not enabled
• Timeout shorter than acceleration time
FAST ISOLATION TEST
To verify Modbus communication:
  1. Open gSender Console
  2. Type:  M3 S12000
  3. Press Enter
Observe:
• Does spindle start?
• Does Alarm 14 trigger immediately?
• Does it start but stop after timeout?
If it starts and runs:
Hardware and Modbus are functioning. Check your post processor.
If Alarm 14 appears:
Configuration mismatch exists in grblHAL settings.
IMPORTING KNOWN WORKING SETTINGS
If configuration drift is suspected:
  1. Export your current firmware settings
  2. Import the PwnCNC provided settings JSON (attached to the bottom of this article)
  3. Reboot controller
This resolves most cases immediately.
gSender VERSION NOTE
Some versions of gSender have demonstrated inconsistent Modbus behavior.
If experiencing persistent Alarm 14 issues:
• Install gSender version 1.5.4 or 1.4.2
• Configure spindle
• Once functioning, upgrading often retains working configuration
   gSender releases can be found here:  https://github.com/Sienci-Labs/gsender/releases
WHEN TO CONTACT SUPPORT
If you still experience issues, email support with:
• Screenshot of gSender Spindle Settings page
• Screenshot of full $$ output
• Photo of Modbus wiring
• Confirmation that spindle runs in manual mode
Incomplete requests may delay troubleshooting.
SUMMARY
If spindle runs in manual mode, hardware is confirmed working.
Alarm 14 indicates a communication timeout between grblHAL and the VFD.
The solution is configuration alignment, not VFD/motor replacement.
5 out of 6 found this helpful
Quick_Start_Guide_-_Sienci_Labs_Super_Longboard.pdf VFD_Programming_for_SLB.pdf SLB-firmware-settings.json